Where is that mediocre person that knows all this stuff? My wife tells me that our smoke alarms are outdated and we can get ones that don't use batteries. Neither one of us belongs on a step ladder 20 feet in the air these days, and if the one in the living room starts chirping at 3:00am neither one of us can do anything about it. We'd have to move out and sell the place, and you know what Las Vegas homes are worth these days. So is there a battery free smoke alarm? I don't see how there could be, and can't find any on line. I did find ones that have a ten year battery good for the life of the alarm, but then it says it still might go off when there is no fire. Do you think I should ask the Las Vegas or Clark County FD?
Reply With Quote Quick reply to this message

 
Old 10-06-2015, 03:15 AM
 
Location: Portland, OR
635 posts, read 745,985 times
Reputation: 454
There are smoke detectors that are hard wired but most homes have to be pre-wired for this option, even those still have battery backup. A lot of newer homes have pre-wired electrical running to all the smoke detectors. Unless you want to spend a lot of money re-wiring I think the 10 year battery life smoke detectors are your only good option. You could even move the smoke detectors from the high locations they are at now and place them closer to the floor so you can reach them if they go off. Good luck.
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 05:32 AM
 
Location: Orange County/Las Vegas
2,536 posts, read 2,735,318 times
Reputation: 2514
The 10 year battery life smoke detectors sound great but after reading the reviews it seems like the batteries haven't been lasting that long.
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 06:17 AM
 
4,862 posts, read 7,960,654 times
Reputation: 5768
A small dog may work too.
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 07:43 AM
 
Location: Sunrise
10,864 posts, read 16,988,924 times
Reputation: 9084
Your insurance company effectively enforces fire alarm code. If you don't have them, and your house burns down, they don't pay.

My policy is crystal clear on several points: I don't do electrical work. (Even easy-peasy electrical work.) If I do, and the house burns down, they don't pay. I have to have a fire extinguisher in the kitchen. If they house burns down and the inspector doesn't find the remains of a fire extinguisher, they don't pay. And I have to have smoke detectors in all bedrooms and strategically placed around the hallways. Or again they don't pay.

I use rechargeable 9V batteries the smoke detector. At least that way when they start chirping, I can swap out the battery and recharge it. I've been doing this for years now and it works well. If it's a wired detector, you can remove the battery entirely and it will stop chirping. But you're on your own with your insurance company.

Putting a smoke detector on a 20-foot ceiling is more of a code violation than not having one. That's unnecessarily dangerous. If everyone in Las Vegas had such a setup it is very likely that dozens of people would fall off ladders and die each year. Here's your solution: move the smoke detector!
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 09:44 AM
 
Location: Vegas, baby, Vegas!
3,977 posts, read 7,636,745 times
Reputation: 3738
I have NEST C02/Smoke detectors in the living room (fireplace), Kitchen and Bedroom.
I have a C02 Detector in the garage, A Fire extinguisher in the Kitchen and by the BBQ.

After 7 years your smoke detector will start chirping, not because the battery is low, because its time
to REPLACE the smoke detector. Most people just disconnect the unit instead of replacing it.

This is a No brainer folks.

Jonathan
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 10:37 AM
 
Location: Silicon Valley
3,683 posts, read 9,858,753 times
Reputation: 3016
Quote:
Originally Posted by Buzz123 View Post
Where is that mediocre person that knows all this stuff? My wife tells me that our smoke alarms are outdated and we can get ones that don't use batteries.
I don't know the codes, but I know how to search for them.

http://www.clarkcountynv.gov/Depts/d...Amendments.pdf

See section R314

If you have an older home, as I do (built in 1988), the fire code at the time the house was built did not require as many smoke alarms as are required now. Current code requires one in every bedroom.

Quote:
R314.3.1 Location. Smoke alarms shall be installed in the following locations:
1. In each sleeping room.
2. Outside each separate sleeping area in the immediate vicinity of the bedrooms.
3. On each additional story of the dwelling, including basements but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level.
My house was built with just two wired smoke alarms, one on each level. Wired smoke alarms still require battery backup, so there really is no such thing as a smoke alarm without a battery. I also have two smoke/thermal alarms connected to my alarm system, so they receive backup power from the alarm system's battery. Everything other smoke alarm in the house is battery powered.

Smoke alarms use either photoelectric or ionization detection, or both (not that common). The alarms I added are either dual-technology, or combo photoelectric/CO detectors. I skimmed an NFPA (National Fire Prevention Association) study on photoelectric vs ionization vs dual-technology detectors, and the conclusion seemed to be that dual-technology had no disadvantages, other than cost, and significant advantages over single-technology detectors. They even outperformed co-located detectors of each type in some cases.

Also note the requirements on CO detection:

Quote:
R314.3.2 Carbon monoxide alarms. Carbon Monoxide alarms outside of sleeping area in the immediate vicinity of the bedrooms in dwellings units within which fuel-fired appliances are installed and in dwelling units that have attached garages.
This thread looks like it's already got a lot of good advice in it for you. Buying the smoke alarms with the long-life lithium batteries, and just replacing them when the batteries die might be a good solution for you.
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 11:02 AM
 
16,711 posts, read 19,404,178 times
Reputation: 41487
Quote:
Originally Posted by Buzz123 View Post
Where is that mediocre person that knows all this stuff?
With that attitude, I hope nobody comes to your aid.
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 11:07 AM
 
Location: Henderson, NV
5,314 posts, read 7,782,804 times
Reputation: 3568
Quote:
Originally Posted by convextech View Post
With that attitude, I hope nobody comes to your aid.
You know he was talking about the poster above you, whose screen name is mediocre, right?
Reply With Quote Quick reply to this message
 
Old 10-06-2015, 11:35 AM
 
16,711 posts, read 19,404,178 times
Reputation: 41487
Quote:
Originally Posted by Raiderman View Post
You know he was talking about the poster above you, whose screen name is mediocre, right?
Oh, I didn't know that. Oops. Sorry.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Settings
X
Data:
Loading data...
Based on 2000-2020 data
Loading data...

123
Hide US histogram


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > U.S. Forums > Nevada > Las Vegas
Similar Threads
View detailed profiles of:

All times are GMT -6.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top